Thread: Switching High Load Devices

  1. #1
    Junior Member
    Join Date
    Jun 2015
    Posts
    8

    Switching High Load Devices

    I am setting up a Caseta system in a small house, and would like to be able to switch on or off two heated towel warmers, these are rated at 1200w each, which is larger than any of the available switches.

    Is there a recommended way of doing this, perhaps pairing a Caseta switch with a higher current relay?

  2. #2
    Senior Member
    Join Date
    Nov 2014
    Posts
    238
    Just use a relay or contractor with a 120v coil. Switch powers coil, relay pulls in, load connects. Depending on how they are wired you could do everything at the panel and replace the current switch with a pico.