Thread: LQSE-2DAL-D can not address the lighting

  1. #1

    LQSE-2DAL-D can not address the lighting

    We have a project that using LQSE-2DAL-D to control DALI Lighting, it is DALI Track Lighting that using Spliter. For 1 transformer connect to 1 Spliter, each spliter connected to 3 tracks, and each track has 3 lights. The problem is there are some lights that can not be addressed, for example on track 1 only 2 lights can be addressed, track 2 only 1 light, track 3 also only 2 lights. i have try to verify wiring before address, the result is the lights that can not be address can not be turn On or Off when i press High End or Off button.

    any advise ?

  2. #2
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    513
    Try the following:

    Force a Full transfer, then go to the Activate Ballasts Tab. On the loop you are having issues, choose to "Activate All ballasts". Does that help resolve your issue? If not, please send in a support file to hwsupport@lutron.com.

  3. #3
    Armando,

    Already send the email, thanks you.

Similar Threads

  1. LQSE-2DAL-D Capacity
    By stevi in forum General Discussion - HWQS
    Replies: 13
    Last Post: 05-29-2016, 02:13 AM
  2. LQSE-2DAL-D & DALI driver issues
    By jwbcinergy in forum Troubleshooting - HWQS
    Replies: 2
    Last Post: 01-25-2015, 08:08 AM
  3. LQSE-2DAL-D issues
    By Masterfader in forum Troubleshooting - HWQS
    Replies: 0
    Last Post: 11-30-2014, 06:04 AM
  4. Programming LQSE-2DAL-D in Homeworks QS
    By Technical Comfort, Inc in forum Programming - HWQS
    Replies: 2
    Last Post: 08-05-2014, 11:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •