Thread: Lutron DFDU Diimmable Receptacle - Electrical Wiring For It

  1. #1

    Smile Lutron DFDU Diimmable Receptacle - Electrical Wiring For It

    Hi,

    I plan on buying 3 Lutron DFDU Dimmable Receptacles and I am wiring the room for them now.

    Do they use the standard 14/2 electrical cables to connect to the Grafik Eye QS?

    Thank you in advance if anyone responds.

  2. #2
    Also, can I daisy chain multiple Lutron DFDU Dimmable Receptacles in a row?

  3. #3
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    It would use just a standard 14/2 Romex or MC cable to wire to the GE. You have to be careful daisy changing as a single zone of a GE cannot exceed 800w and the total for the GE unit cannot exceed 1920W (if powered with a 20a circuit).
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

Similar Threads

  1. Keypad wiring redundancy
    By Ty W. in forum Best Practices - HWQS
    Replies: 12
    Last Post: 04-22-2018, 11:06 PM
  2. Adding a keypad to RadioRa2 system - electrical requirements?
    By geofry in forum Design Assistance - RA2
    Replies: 5
    Last Post: 09-30-2014, 05:38 PM
  3. Qed shade wiring
    By Anytech in forum General Discussion - Legacy QED
    Replies: 4
    Last Post: 08-25-2014, 09:33 AM
  4. 0-10V wiring with an RPM
    By cabethesda in forum General Discussion - HWQS
    Replies: 1
    Last Post: 08-05-2014, 08:16 PM
  5. QS & shade wiring
    By Tony Sena in forum Best Practices - HWQS
    Replies: 1
    Last Post: 06-26-2013, 06:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •