    Qse-io

    Are you able to programme both the NO and NC contacts on the QSE-IO. It is in position 11 on the second cabinet and when assigning it just gives the option of 11-1 to 11-5 ie the the five outputs, but not options for the NO and NC on each output.

  2. #2
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    513
    You can program the 5 Contact closure inputs as normally open, or normally closed, but only those five inputs can be programmed in the system. In the same way, you can default your contact closure outputs to system buttons to have them open on the press on and close on the press off to simulate normally closed behavior, and do the reverse for normally open behavior.