PD-6ANS Not turning LEDs all the way off...
Moved a PD-6ANS from one room to another. Same LEDs in both rooms. Old room worked fine. New room the lights turn almost all the way off but there's still a hint of light coming from them. I know on the dimmers you can adjust the low end trim to fix this, but on this on/off switch is there any way to fix this?
Thanks!
23V between load and neutral when off ?!?
Quote:
Originally Posted by
Brian W.
Still use the neutral on the PD-6ANS. Just use this in addition to the switch.
1. With unknown or untested LEDs, it could be multiple factors. I've had many cases where it's been: "it works fine with 3 of these LEDs, but it's not working correctly with 6 of the same LEDs (or vice versa)".
2. It's our best guess at it working. With the huge variety of LEDs being manufactured nowadays, we don't have the manpower to test them all. The PD-6ANS switch always works fine with incandescent or halogen bulbs. With the way digital dimmers/switches work, there can still be a very small amount of voltage on the output of the switch, even when the switch is off, to keep the microchip running. Incandescent or halogen bulbs aren't affected by this small voltage, but some LEDs are sensitive enough to pick up on this voltage and stay lit at a very dim level. The LUT-MLC helps with this small voltage.
I have a chandelier with 3 Philips Warm Glow LEDs, which should be compatible. I am also having the problem with dim illuminatin when the PD-6ANS is "off". When it is "off" I am measuring about 23VAC between the load and neutral. That is a lot of voltage for it being "off". Is my unit defective? And, if I were to add a LUT-MLC, and that fixed the problem, how much power leakage would I experience while it was "off"?
thanks.