RRD-PRO blinking indicator lights 3 and 7 but is wired correctly.
I have a RA2 system that we commissioned around a month ago. Was programmed with 12.6 software. I get a call from the builder that a chandelier in the Master Bath is no longer working and the dimmer is blinking. Arrive and find IL 3 and 7 blinking. Also the dimmer would not turn on the load. Manual says this means the line/load miswire detected. This system has been working fine for a month. I am doubting at this point that it's miswired. I pull FASS and reset and it starts working fine. I find another RRD-PRO dimmer doing the same pattern and not working either (2 sconces) . Reset with FASS and it starts working again. At this point I call tech support and they said that IL blinking 3 and 7 could mean nothing else but miswired line/load. I get a case # and end the call. I pull the dimmers and verify they were not miswired. I disconnect the black wire on the black terminal and there is 120 volts on the wire and not the terminal. And no voltage on the brass terminal with the other black wire on it. So not miswired. Has anyone else seen this happen? My fear is that it's going to happen again and I or Lutron don't know why it's happening. The only other clues I can give are that both of these dimmers are fed by the same breaker and also that it is lightning season here right now. Thanks