If I design a system using the phase adaptive DPMs for QS, if any particular zone might exceed 1 amp can I use a PHPM-PA-120-WH?
I don’t see DPM panels in the QS 9.3 software. Those are custom for now?
Printable View
If I design a system using the phase adaptive DPMs for QS, if any particular zone might exceed 1 amp can I use a PHPM-PA-120-WH?
I don’t see DPM panels in the QS 9.3 software. Those are custom for now?
Dear Tony,
Thank you for the information.
The HomeWorks QS software currently does not have the DPM panels for the LQSE-4A1-D modules.
Can you tell us what application you would be using these for? Would you be able to use a HW-RPM based solution instead of the LQSE-4A1-D modules and PHPM modules?
Because the WPM6 does not have phase adaptive outputs I can not imagine specifying it unless I completely controlled the selections of connected loads. I do think there is a major hole in the product line for multi zone phase-adaptive control without having to support the added infrastructure & physical size of panels & modules.
The LQSE-4A1-D seems to solve this, however it comes with too many caveats to really be useful in a broad sense.
We continue to design & specify every system with panels, however at times it feels over designed and unnecessary. That being said it has been such a solid solution, it would take some very special hardware to move away from it.